If a 20 slot panel is full and no maximum number of CBs can be found on the panel cover, can you install tandems? How many? Common sense?
Circuit Total Limiting (CTL) panel / breaker combinations probably came in after 1965.And some panels restrict the actual location that tandems can be placed in, by use of exclusion features on the bus and/or breakers.
NEC 1965 384-15 (2nd paragragh) said:A lighting and appliance branch circuit panelboard shall be provided with physical means to prevent the installation of more overcurrent devices than that number for which the panelboard was designed, rated, and approved.
And in addition to the 'label denoting specifications' for the panel, we can often at least find a hint in the original 'label for breaker purposes' directory, either with 'a' or 'b' on some numbered lines, and/or dashed lines to imply dual labels in one space.The panel label (if present and readable) will show location and max numbers of tandems allowed.
Of course the general rule is no- 110.14(A), but the rep. is right, for the Equipment Grounding Conductors, usually, with some restrictions about sizes. But not for Grounded Conductors.My Square D rep. told me that Square D QO breakers are rated for two conductors under one screw.
Is that correct?
My Square D rep. told me that Square D QO breakers are rated for two conductors under one screw.
Is that correct?
http://static.schneider-electric.us/assets/digest/load-centers.pdf
My Square D rep. told me that Square D QO breakers are rated for two conductors under one screw.
Is that correct?
I am having a hard time understanding what this has to do with the original question, but the quick answer is yes depending on the wire size, wire type, and breaker rating. 10A-30A is rated for (2) #14-#10 CU. Reference page 2 on the link below for more information.
Code:http://static.schneider-electric.us/assets/digest/load-centers.pdf