How many conductors are allowed in 3/8 inch LTFMC?

Status
Not open for further replies.

joe tedesco

Senior Member
Would it be a violation if I used any other type of insulations that are not listed here in this table? I found only 13 types?

This Table is taken from the 1999 NEC.

Courtesy: www.nfpa.org

000085_G.jpg
 

mwdkmpr

Member
Re: How many conductors are allowed in 3/8 inch LTFMC?

Use chapter 9 tables 4&5 to calculate # of wires.

Also note that 3/8" is limited to the uses shown in 348.20(A).
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: How many conductors are allowed in 3/8 inch LTFMC?

Joe,
348.22 permits the use of either the Chapter 9 Table 1 percentages or Table 348.22. This would mean that you are not limited to the types of insulation listed in Table 348.2
Don
 