Its a display case for make up and there are 4 foot sections for each 120/12 volt transformer. The people at the store are wanting to put more than one four foot section on the transformer.
Usually these are rated watts per foot-- need to know that.
Not just the transformer, the light strip too!Ok I will have to look at the transformer and let you know.
Its a display case for make up and there are 4 foot sections for each 120/12 volt transformer. The people at the store are wanting to put more than one four foot section on the transformer.
Usually these are rated watts per foot-- need to know that.
I think finding out the manufacturer/model of the LED strip will solve your problems. There has to be some kind of info on the device. GoldDigger is right about the wattage. Usually, a strip in a 4' section is going to be around 15w. How do they tie in to the driver? Is this like a fluorescent lamp or is it a plastic strip?
Until they're not - usually when you're looking it up with a customer and you realize the manufacturer has one rating on the module, another in the catalog and you're standing there without a calculator...
I noticed today on the cord to the transformer there is a tag that says 120 volt/ 7amps, I didn't realize LED's pulled that much. To answer your question about the wattage the only thing I saw was inside the instructions, it mentions it as the "60 watt transformer". If its 7 amps per every 4 foot, there is only one circuit there with a receptacle and a power strip plugged in and the store is wanting me to put all 24 foot on that one circuit. Looks like Im going to have to break it to them that they need more circuits.
I noticed today on the cord to the transformer there is a tag that says 120 volt/ 7amps, I didn't realize LED's pulled that much. To answer your question about the wattage the only thing I saw was inside the instructions, it mentions it as the "60 watt transformer". If its 7 amps per every 4 foot, there is only one circuit there with a receptacle and a power strip plugged in and the store is wanting me to put all 24 foot on that one circuit. Looks like Im going to have to break it to them that they need more circuits.