The house has Insulated Concrete Form walls and a surface mount panel seems to be in order. Due to the number of homeruns, it seems we don't have enough punch-out holes. We're thinking of using a pull box next to the panel and then putting say 2-3 NM cable through short nipples into the panel.
Given the short distance of conduit, is there a way to justify not having to derate the conductor ampacity. (If we ran 3 cables we'd have to derate to 80%, if we ran 4 cables we'd have to derate to 70%)
Given the short distance of conduit, is there a way to justify not having to derate the conductor ampacity. (If we ran 3 cables we'd have to derate to 80%, if we ran 4 cables we'd have to derate to 70%)