My local utility can support up to 1200A 208/120V 3 phase service from a pole mounted type transformers. Their biggest pole mounted transformers are 167KVA. How is this typically done? Lets assume i have maximum demand of 424KVA Based on the maximum demand for a 1200 3 phase 208/120 gear. Do they typically add 3 167KVA transformers on the same pole? or do they put them on separate poles? (assuming pad mounted transformer is not an option) Thank you,
A facility that I work with has a 1600A 480V three phase service.
The utility provisioned 3 250kVA pole mount transformers on a single pole in front of the building.
It is possible that the transformers are smaller than 250kVA; I'm not going by their nameplate but by the '250' label at the bottom of the cans.
-Jon
I did an overhead 480 service a 5 years ago that they served with 3x167's. There is 13.2kv->4800 step down bank in Cooperstown that consists of 3x300's on a single pole. That pole is hating life. I dont think I have ever seen 3X500's on a single pole, but lots of those on two pole platforms around here. user @mbrooke had some good pics of overloaded poles, but he hasn't been around in a while, and i cant find the old thread.
It also depends on the class of pole. But if your calculated NEC load is 424 kVA, it's likely that the utility will install something smaller than than 3 x 167 kVA due to the inherent conservatism of the NEC load calculations.