wehaveplans
Member
- Location
- Seattle, WA
Hi everyone!
We are designing a very purpose built data center for a customer who does not need a secondary PUD feed or UPS battery backup systems. This is a long term storage (LTS) back up site. Our capacity plans for a 4.4mVa data center; backup servers are extremely dense and require a ton of potential energy. There will be 8 aisle of server racks in which we are planning on installing one busway systems per two rows of server racks, a total of 4 busway systems. We are planning on sourcing a European 13.2kV/415Y 5000 kVa transformer since we have PDU's that feed each phase to neutral resulting in 240v single phase without any secondary transformers. Each of our busway systems are 18 meters in length and are sized at 1200 amps (415v 4W L-N).
We are planning on having fusible disconnects that directly feed into the busway system. Do we need a distribution panel feeding the disconnects, or can we hook four fusible disconnects directly into the transformer in this configuration? The transformer is outside of the building 8 to 10 meters away from where the fusible disconnects will be located. 16 feed wires will be significantly cheaper in T&M than massive switchboard or distribution panels.
Thanks in advance for the help and let me know if I didn't include any information.
We are designing a very purpose built data center for a customer who does not need a secondary PUD feed or UPS battery backup systems. This is a long term storage (LTS) back up site. Our capacity plans for a 4.4mVa data center; backup servers are extremely dense and require a ton of potential energy. There will be 8 aisle of server racks in which we are planning on installing one busway systems per two rows of server racks, a total of 4 busway systems. We are planning on sourcing a European 13.2kV/415Y 5000 kVa transformer since we have PDU's that feed each phase to neutral resulting in 240v single phase without any secondary transformers. Each of our busway systems are 18 meters in length and are sized at 1200 amps (415v 4W L-N).
We are planning on having fusible disconnects that directly feed into the busway system. Do we need a distribution panel feeding the disconnects, or can we hook four fusible disconnects directly into the transformer in this configuration? The transformer is outside of the building 8 to 10 meters away from where the fusible disconnects will be located. 16 feed wires will be significantly cheaper in T&M than massive switchboard or distribution panels.
Thanks in advance for the help and let me know if I didn't include any information.