How Many Single Conductors In Ladder Type Tray

Status
Not open for further replies.

SWILLIAMSON

New member
Location
Ashland KY USA
I am feeding two MCCs from two different breakers in a 480V Switchgear through the same tray. The breakers are 1200A. I'm running (4) 500 kcmil per phase and (2) 500 kcmil grounds per circuit, 28 cables total, through aluminium ladder type tray. I'm confused, if I run these in a single layer, do I need to keep a space the diameter size of the cable between each cable, or can I run these single layer with them touching? What are my options?
 
Last edited:
I am feeding two MCCs from two different breakers in a 480V Switchgear through the same tray. The breakers are 1200A. I'm running (4) 500 kcmil per phase and (2) 500 kcmil grounds per circuit, 28 cables total, through aluminium ladder type tray. I'm confused, if I run these in a single layer, do I need to keep a space the diameter size of the cable between each cable, or can I run these single layer with them touching? What are my options?

Is this for an industrial application?
 
I am feeding two MCCs from two different breakers in a 480V Switchgear through the same tray. The breakers are 1200A. I'm running (4) 500 kcmil per phase and (2) 500 kcmil grounds per circuit, 28 cables total, through aluminium ladder type tray. I'm confused, if I run these in a single layer, do I need to keep a space the diameter size of the cable between each cable, or can I run these single layer with them touching? What are my options?
You can run them in a single layer touching or spaced, or you can run them triplexed, touching or spaced. What comes into play is conductor ampacity as a result of how you run them. I'll let you try to figure that out. But if you have a problem with doing so, do not hesitate to post again.

Why are you running a 500kcmil EGC per feeder when only 3/0 copper is required? Just to keep all conductors the same size?