T Twillows Member Location Minnesota Occupation Electrician Nov 23, 2022 #1 How many wires can I put through one knocked out hole in industrial panel board? All #10s 480v lighting panel board.
How many wires can I put through one knocked out hole in industrial panel board? All #10s 480v lighting panel board.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Nov 23, 2022 #2 What's in the hole a nipple? Welcome to the Forum.
T Twillows Member Location Minnesota Occupation Electrician Nov 23, 2022 #3 It's going to be a chase nipple or just a plastic bushing from a gutter below the panel board.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Nov 23, 2022 #4 A nipple can be filled to 60%.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Nov 23, 2022 #5 None. Wires must be installed in raceways and cannot be run through holes.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Nov 23, 2022 #6 don_resqcapt19 said: None. Wires must be installed in raceways and cannot be run through holes. Click to expand... He did mention a chase nipple.
don_resqcapt19 said: None. Wires must be installed in raceways and cannot be run through holes. Click to expand... He did mention a chase nipple.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Nov 23, 2022 #7 infinity said: He did mention a chase nipple. Click to expand... did not see his second post