how exactly would you calculate the current carring capacity of 500mcm cable but with 9conductors, three runs of conduit so 3 paralleled
runs i guess,
looking it up in 310 I see 430 amps, (thhn)
and multiply it times 3, to get 1290, is this then (three phase 480) is this then the total amps per phase with this conductor?
thanks clay.