I'm wiring residential house and was wondering how many 12/2 romex can I pass thru a 1 inch hole in 2x4 wall stud by code.
You can derate from the 90 deg column. You could have 4 cables, which would be 8 CCC. #12 would be 30A under the 90 deg column. 8 CCC would require a 70% deration. 30A x 70 = 21A. #12 would still be good for a 20A circuit.Currently under 2008, but the way I read is - Table 310(B)(2)(a) states that 3 NM cables would be 6 current carrying conductors and 80% of rating on cable. 12 gauge is listed as 25 amp(?) which after adjustment, still maintains 20 amp allowance which is also regulated under 240.4(D). Am I looking at that correctly? Inspector still trying to learn after 30 years.
I get the "rule of thumb" on this one but I wonder why the guys making these rules say no more than 2 or 3 cables, it must be because they don't understand the actual code either. If they said keep it at 4 cables or less then they would be demonstrating that they understood the actual requirment.In my experience the "no more than......" "rule" developed due to the difficulty some folks have in understanding the derating concept.
Unfortunately in this area there are several "rules" inspectors quote (such as "no more than 3; always drive 2 rods, etc.) simply to avoid 'teaching' Code to those not wishing to learn.
I think the big problem is code ignorance. Many people read the part in 334.80 that reads "where more than 2 NM cables...are installed....in the same opening in wood framing....the allowable ampacity of each conductor shall be adjusted...." BUT they stop there and dont do the actual adjustment to find it doesnt effect you until over 9 CCC with #12 and #14. Also there is common ignorance that "You cant use or derate NM at 90 degrees....." I seriously wonder of some of these people ever actually open the code book.I get the "rule of thumb" on this one but I wonder why the guys making these rules say no more than 2 or 3 cables, it must be because they don't understand the actual code either. If they said keep it at 4 cables or less then they would be demonstrating that they understood the actual requirment.![]()
Yeah and another thing often overlooked is the "without maintaining spacing" part in bundling.What most people overlook is the part that says "where firestopped" then you must derate for more than 2 cables. It doesn't say any hole with more than 2 cables, only where they used firestop.