yomatt
Member
- Location
- Arlington, VA, USA
- Occupation
- RF Engineer
My customer has two banks of DC rectifiers (minimum input 185V) with 12 kVA and 24 kVA maximum loads to be connected line-to-line on a 120/208 3ɸ service.
There are de minimis single phase loads. 120/240 1ɸ isn't available.
I calculate 150, 50, 100A on each phase, using panel VA addition, or 153, 58, 115A using phase current math.
This is pretty unbalanced, but is it enough to bother the utility servicing the installation?
Is 200A service adequate? (it seems to me it is)
The reach alternate is to step the voltage up to 277/480 and re-wire the rectifiers balanced on 3ɸ.
Of course this is costly, so would rather avoid it unless there is no choice.
Bonus question: does the answer change if taking house power from a facility that has 3ɸ motors on the same branch? (I think yes)
First time posting, so take it easy on me