How Terminate 6/2 MC Into Old Work?

Status
Not open for further replies.

dafish

Member
Location
Illinois
Occupation
Project Manager
I don't see anything larger than the 3/8" Bridgeport double-snap, and that's too small for 6/2MC. Any ideas?

Thanks!
 
Try and imagine how big that connector would have to be. What size box are you using? You will never be compliant with 2- 6/2 mc cables and a device.

Tell us more what you are doing.
 
You will need to get a connector based on the OD of the cable.
An example would be 6-2 g mc
OD= .755. find a connector for mc that has a range to which this fits.
 

Attachments

  • Screenshot_20230328-163057.png
    Screenshot_20230328-163057.png
    52.8 KB · Views: 9
  • Screenshot_20230328-163321.png
    Screenshot_20230328-163321.png
    99 KB · Views: 14
I'd use old work without clamps and use 3/4 MC connector. not a a queeze but double screw clamp. These larger wire MC can be very small
 
dafish, please update your profile to show the state you are located in at a minimum for your location
 
Locations: Illinois. I'm in an area using pretty old code (2014 at the newest), but I keep an eye on best practices.

Doing: This will inflame some, but I've noted way too many "electricians" in Illinois (which has few test/certification requirements) doing work that doesn't meet code/best practice. I'm checking off a few things to make sure I'm getting a quality plan and how to recognize the real deal guys when I see/hear it.

High Level Objective: I'm installing one or two (cost) 60 amp circuits for hardwired EV use. I require 6/2 TTHN in conduit, be it flexi, MC, etc.

Problem: Load center is in finished garage, fluish mounted to wall. How to land conduit to panel wo/cutting drywall is only real hurdle remaining.

Thanks,

-d
 
Problem: Load center is in finished garage, fluish mounted to wall. How to land conduit to panel is only real hurdle remaining.
Only way is to open the wall somewhere on the top, bottom or a side of the panel. Then patch it. Depends on how and where the cables or conduits need to be run. This is not small stuff.

Any competent electrician should be able to do that for you.

-Hal
 
  • Like
Reactions: J2H
Put a large jbox maybe 8x8 right above panel go from flex from panel to jbox then your Mc. Not much else to do
 
It might be long term more useful, and cheaper when finish work is considered, to cut a hole in the drywall and install a permanent access door, rather than patching. (Note: consider firewall requirements if you do this)

Jon
 
Status
Not open for further replies.