I want to make sure, that I am doing this right. Please scold me, if not. I have a 480V 3 phase compressor. It has a 125 hp 3ph pump motor, and a 10 hp 3ph fan motor. I am taking 156A(NEC 430.250) for the main motor, and 14A(NEC 430.250) for the fan motor and combining them. For a total of 170A per NEC. I am multiplying this by 1.25 for continuous load to get 212.5A. I am using this in the 75deg column of 310.15b16 and coming up with 4/0 for my conductors, no temp derate. I am using the NEC total of 170A and multiplying by 2.5 for inverse time breakers, and getting 425A. Going up to a 450A OCPD. And using a #2 EGC per 250.122. does this all seem right? I will be using adjustable trip breakers, or should I just use fixed trip?
Thanks for any help. or Scoldings.