how to calculate apparent power ratings

Status
Not open for further replies.

mari

New User
Location
FL
Hello,

Anybody can help me with the following problem:
say you have a building that needs 208Y/120. The utility primary distribution is12.47KV. On the problem they give you the single phase load 30 W at .95 lagging and also they give you three phase load 150 at .98 lagging.
Why on the solution they add 30W + 150W to get the total active power. Also they add the reactive power by single phase and 3 phase. Then they divide it by 3 to get rating for each transformer.
The formula that i dont get is that they add single phase power and three phase power together, never seen that before..
Anybody know why?

Thanks in advance
 

Ingenieur

Senior Member
Location
Earth
Because it is all in watts
I assume you meant kw?

S va = P w + jQ var
where:
P = cos ang x S
Q = sin ang x S
cos ang = pf

total P = 180 kw

Find S kva for each
3 ph: S = 150/0.98 = 153.1 kva
1 ph: S = 30/0.95 = 31.6 kva
total S 184.7 kva

Find ang for each
ang = arccos pf
3 ph 11.5 deg
1 ph 18.2 deg

Find Q var for each
Q var = sin ang x S
3 ph 30.5 kvar
1 ph 9.9 kva
total Q 40.4 kvar

Total
184.7 kva = 180 kw + j40.4 kvar = 184.7/12.65 deg
 

Smart $

Esteemed Member
Location
Ohio
Welcome... :thumbsup:



Who are they? :roll:

Should we assume the single phase load is balanced (as it appears, Ingenieur already has).


Personally, all I would have done is this...
...
Find S kva for each
3 ph: S = 150/0.98 = 153.1 kva
1 ph: S = 30/0.95 = 31.6 kva
total S 184.7 kva

...and divided by 3.
 
Last edited:

Ingenieur

Senior Member
Location
Earth
Welcome... :thumbsup:



Who are they? :roll:

Should we assume the single phase load is balanced (as it appears, Ingenieur already has).


Personally, all I would have done is this...

...and divided by 3.

I wanted him to see the concept and relationship of S, P and Q
makes it easier to derive any qty once the overall relationship is grasped
 

Sahib

Senior Member
Location
India
Because it is all in watts
I assume you meant kw?

S va = P w + jQ var
where:
P = cos ang x S
Q = sin ang x S
cos ang = pf

total P = 180 kw

Find S kva for each
3 ph: S = 150/0.98 = 153.1 kva
1 ph: S = 30/0.95 = 31.6 kva
total S 184.7 kva

Find ang for each
ang = arccos pf
3 ph 11.5 deg
1 ph 18.2 deg

Find Q var for each
Q var = sin ang x S
3 ph 30.5 kvar
1 ph 9.9 kva
total Q 40.4 kvar

Total
184.7 kva = 180 kw + j40.4 kvar = 184.7/12.65 deg
Wont the 184.7 kva transformer size undersized for any future expansion
because per phase 3 phase load=153.1/3 and single phase load=31.6kva and so total per phase load={153.1/3)+31.6. So total three phase load=3*[{153.1/3)+31.6]=248kva?
 
Last edited:

Smart $

Esteemed Member
Location
Ohio
Wont the 184.7 kva transformer size undersized for any future expansion
because per phase 3 phase load=153.1/3 and single phase load=31.6kva and so total per phase load={153.1/3)+31.6. So total three phase load=3*[{153.1/3)+31.6]=248kva?
Assume the OP means total single phase load (30kW) on all three phases (10kW each).

I already asked about unbalanced single phase load with no reply.
...
Should we assume the single phase load is balanced (as it appears, Ingenieur already has).
...
 

Ingenieur

Senior Member
Location
Earth
Wont the 184.7 kva transformer size undersized for any future expansion
because per phase 3 phase load=153.1/3 and single phase load=31.6kva and so total per phase load={153.1/3)+31.6. So total three phase load=3*[{153.1/3)+31.6]=248kva?

I did not size the transformer
only determind the load
 