How to calculate the summer and winter power consumption?

Status
Not open for further replies.

jaehlee99

Member
Location
Canada
Hi Forum,

I appreciate your help as always.

I am counting the power consumption, for example, unit 12.

- winter : 208V x 0.77A = 160W
- summer : 208V x 9A = 1872W

Is that right calculation?

Please see attached file.

Thanks in advance
James
 

Attachments

  • QUESTION2.pdf
    86.2 KB · Views: 0

Ingenieur

Senior Member
Location
Earth
Thank for your reply.

If Summer is not, how can I expect the power calculation with data sheet?


You used the ckt size
add up cond fan + evap fan + comp fla's

all results are in va not watts because the power factor is not considered
va should be used for ckt sizing anyways
 

jaehlee99

Member
Location
Canada
You used the ckt size
add up cond fan + evap fan + comp fla's

all results are in va not watts because the power factor is not considered
va should be used for ckt sizing anyways

I appreciate your help.

cond fan + evap fan + comp fla's = 0.5+0.77+5.6=6.87 A

MCA = 1.25 x (cond fan + evap fan + comp fla's) = 1.25 + 6.87 = 8.56 A

This is similar to MCA 9A in the data sheet. I might be wrong calculation. Would you please advise me ?
 

Ingenieur

Senior Member
Location
Earth
I appreciate your help.

cond fan + evap fan + comp fla's = 0.5+0.77+5.6=6.87 A

MCA = 1.25 x (cond fan + evap fan + comp fla's) = 1.25 + 6.87 = 8.56 A

This is similar to MCA 9A in the data sheet. I might be wrong calculation. Would you please advise me ?

Correct
power consumption 6.87 x 208(?)
if in a home are you sure it's not 230?
208 is usually a 3 phase voltage


correct on the mca
iirc actually 1.25 x largest + sum of other motors
in this case doesn't make much of a difference
might be a small amount for controls too
 
Last edited:

jaehlee99

Member
Location
Canada
Correct
power consumption 6.87 x 208(?)
if in a home are you sure it's not 230?
208 is usually a 3 phase voltage


correct on the mca
iirc actually 1.25 x largest + sum of other motors
in this case doesn't make much of a difference
might be a small amount for controls too

Thanks

When sizing circuit breaker, is it same as MCA ?
 

kwired

Electron manager
Location
NE Nebraska
Thanks

When sizing circuit breaker, is it same as MCA ?
MCA is for determining minimum size of conductor needed. If it has across the line starting of compressor - the minimum setting of short circuit/ground fault protection will be higher then MCA.

Actual load will be less then MCA, actual load will depend on conditions present at time you measure load as well, if the unit is working harder, has plugged coils, filters it will have an impact on actual load. For calculations though you should assume it can draw as much as RLA of compressor plus FLA of other motors that will run simultaneously.
 

JFletcher

Senior Member
Location
Williamsburg, VA
Hi Forum,

I appreciate your help as always.

I am counting the power consumption, for example, unit 12.

- winter : 208V x 0.77A = 160W
- summer : 208V x 9A = 1872W

Is that right calculation?

Please see attached file.

Thanks in advance
James

This is a Carrier vertical PTAC, yes? In heat pump mode, the power consumption is going to be the same winter or summer. If it has electric heat, it will use more power in winter than summer.

Cooling
On a call for cooling, the condenser fan and evaporator
blower are energized simultaneously. After 10 seconds the
compressor will energize.

Heating (heat pump units)
On a call for heating, the condenser fan and evaporator
blower are energized simultaneously and after 10 seconds
the compressor will energize.

Page 15 here:

http://www.americancoolingandheatin...rrier-product-data-specifications/52v-2pd.pdf
 

kwired

Electron manager
Location
NE Nebraska
This is a Carrier vertical PTAC, yes? In heat pump mode, the power consumption is going to be the same winter or summer. If it has electric heat, it will use more power in winter than summer.

Cooling
On a call for cooling, the condenser fan and evaporator
blower are energized simultaneously. After 10 seconds the
compressor will energize.

Heating (heat pump units)
On a call for heating, the condenser fan and evaporator
blower are energized simultaneously and after 10 seconds
the compressor will energize.

Page 15 here:

http://www.americancoolingandheatin...rrier-product-data-specifications/52v-2pd.pdf
I agree, but will add that summer load is usually higher only because the unit is working harder. It is still same capacity unit so rating is still same heating or cooling, but on a really cold day there isn't as much heat in the outdoor air to absorb and actual load on the unit drops because it is moving less heat.

But for branch circuit/feeder/service calculations the full rating of the unit is what matters. And yes if there is backup resistance heat it is very likely higher load then the heat pump.
 