Go to chapter 9 for conduit and wire dimensions, the number of conductors allowed in the conduit will be the same regardless of any derating.

Roger
 

bora43

Member
How to calculate

How to calculate

I installed 20 #12 THHN in 1" EMT 10 ckts, all dedicated. Inspector sad that I violated the NEC. He sad it should be no more then 4 #12 conductors in 1" EMT because of derating factor. Any one knows the answer?
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
I installed 20 #12 THHN in 1" EMT 10 ckts, all dedicated. Inspector sad that I violated the NEC.

See T310.15(B)(2)(a) if you have them all on 20A breakers.

He sad it should be no more then 4 #12 conductors in 1" EMT because of derating factor.

My guess is he meant 4 circuits with their own neutrals.
 