How to check the Selective coordination settings at field?

Status
Not open for further replies.

mathan1987

Member
Location
Seattle
Occupation
Electrical design engineer
How to check the switch board and panel board breakers for the selective coordination setting at field?
 

ron

Senior Member
Do you want to test the selectivity between breakers, such as zone selective interlock? The manufacture will have specific instructions how to test their breaker combinations.

If you want to check individual breaker settings, you can do either primary injection testing or secondary injection testing.
 

topgone

Senior Member
Ask for documents from owner. Companies maintain records of relay settings and coordination plots as well as equipment ratings.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
How to check the switch board and panel board breakers for the selective coordination setting at field?
Do you want to check it or test it? Checking it would imply that you are looking to make sure that whoever did the selective coordination design documented it somewhere and the settings on that document match what is in the field.

Should not be real hard to find that document and do that kind of checking.
 

mathan1987

Member
Location
Seattle
Occupation
Electrical design engineer
I wanted to know how to check the time settings on the breakers at site done per the design documents.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I wanted to know how to check the time settings on the breakers at site done per the design documents.
That depends on the breaker.older units had dials which you could look at, most probably have a display you need to scroll through, and some require computer software and a communications connection.
 