fuse_junkie
- North Carolina
- Electrical Engineer
Hello. I'm working on a town hall hvac renovation and I'm trying to verify that the panels/service can handle the new equipment. 220.87 says to make sure (existing loads x 1.25) + new loads < feeder/service rating. Am I still able to use this method when I'm replacing potentially half or more of that existing load with new equipment? I was floating the idea of taking (existing load x 1.25) - (connected load value of existing equipment to be removed) + (new continuous loads x 1.25) + (new non-continuous loads) and making sure that value doesn't exceed the feeder/service.
My confusion is that if I measure the existing load and just add the new load, I'm double counting a lot of equipment. On the flip side, I don't see where the NEC specifically allows me to do what I'm proposing above (at least in 220.87).