fuse_junkie
Member
- Location
- North Carolina
- Occupation
- Electrical Engineer
Hello. I'm working on a town hall hvac renovation and I'm trying to verify that the panels/service can handle the new equipment. 220.87 says to make sure (existing loads x 1.25) + new loads < feeder/service rating. Am I still able to use this method when I'm replacing potentially half or more of that existing load with new equipment? I was floating the idea of taking (existing load x 1.25) - (connected load value of existing equipment to be removed) + (new continuous loads x 1.25) + (new non-continuous loads) and making sure that value doesn't exceed the feeder/service.
My confusion is that if I measure the existing load and just add the new load, I'm double counting a lot of equipment. On the flip side, I don't see where the NEC specifically allows me to do what I'm proposing above (at least in 220.87).
I'd appreciate it if anyone can offer some advice.
My confusion is that if I measure the existing load and just add the new load, I'm double counting a lot of equipment. On the flip side, I don't see where the NEC specifically allows me to do what I'm proposing above (at least in 220.87).
I'd appreciate it if anyone can offer some advice.