I have a molded case circuit breaker feeding a VFD and control power transformer in my VFD cabinet. VFDs and breakers are different sizes, anywhere from 60A to 500A at 480V. My question is: what is the best way to tap off load side of breaker to control power transformer? For example, in my 100HP VFD cables are 2/O which are terminated in 200A breaker, so far so good. But I also need to connect 2 control power transformer cables which are 14AWG in load side of the breaker to feed a single phase 480:120V control transformer. We are currently using a certain brand of breaker which comes with quick disconnects (see picture) that I can terminate my female disconnects. But I am considering using a different type of breaker that does not have the option of quick disconnects for smaller wires. In this case, what is the best way to connect the small 14AWG wires to breaker? it is a UL508 enclosure.