CaptKarnage
Member
- Location
- Milwaukee, WI
- Occupation
- Electrical Engineer
I work with large industrial furnaces. We use 200 degree C SRML wire for a lot of devices where the wiring needs to get close to the furnace. I'm waiting on a survey to find out what the actual maximum ambient temperature is close to the furnace. If it turns out it's below 80 deg C, then I don't have an issue. But, if we have ambient temperatures above 80 deg C close to the furnaces where some of these cables are run, how do I derate? Is there a formula behind the NEC tables that can be used for higher temperatures? I would really like to do a "worst case" calculation because the survey may not be done in time for the project.
Background: due to construction, we are having to reroute cable and conduit and in order to fit all conductors into the same conduit we would like to decrease the wire gauge. It's only a 5A circuit, so the electrician doesn't seem concerned, but at high temperatures, it can derate by qutie a bit. I'm using the manufacturer's listed ampacity at 30 degrees C, and for the size, number of conductors and 80 deg C, my derating is down from their listed 40 A to 8.2A and I need to figure out how much further I need to derate if my ambient gets above 80 deg C.
Note: this is not internal wiring in the furnace, this is wiring adjacent to the furnace and does come from feeders normally covered under NEC.
Background: due to construction, we are having to reroute cable and conduit and in order to fit all conductors into the same conduit we would like to decrease the wire gauge. It's only a 5A circuit, so the electrician doesn't seem concerned, but at high temperatures, it can derate by qutie a bit. I'm using the manufacturer's listed ampacity at 30 degrees C, and for the size, number of conductors and 80 deg C, my derating is down from their listed 40 A to 8.2A and I need to figure out how much further I need to derate if my ambient gets above 80 deg C.
Note: this is not internal wiring in the furnace, this is wiring adjacent to the furnace and does come from feeders normally covered under NEC.