how to determine 3 phase panel with a grounded hot leg, panel has three legs a,b,c

Status
Not open for further replies.

luisaguirre

New member
Location
moreno valley,ca
measured A to ground 123 volts

measured B to ground 247 volts

measured C to ground 123 volts

measured A to C 247

if so has does a phase inverter work, because i need 400 volts to operate dovetail machine
 
May be too early for my brain, but those numbers only make sense to me if you had an ungrounded delta. In any event, with a phase to phase voltage of 247, you will no get your desired 400 volts.
 
measured A to ground 123 volts

measured B to ground 247 volts

measured C to ground 123 volts

measured A to C 247

if so has does a phase inverter work, because i need 400 volts to operate dovetail machine

If you have voltage to ground on all three lines - I would say none of them are grounded because if one of them were I would expect one of your readings to be zero or very close to zero. What do you have from A-B,B-C?

Your readings sound more like it may be a 120/240 single phase system with grounding/bonding issues, or you have a delta system with a high leg, but if that were the case the voltage from B to ground should have been lower, probably should be around 213 if A to C is 247. I'm leaning more toward the high leg system, except the B to ground voltage is not possible but everything else is.

Not sure what you are asking for certain about phase inverter to get 400 volts, seems to me you need a transformer to get what you appear to be looking for.
 
Last edited: