I've searched around a bit and can't find a clear answer or much information on this anywhere.
UL508a Section 49.2 (Supply Ratings)
How does this apply to multi-phase systems? Currently, we just total up all the loads, regardless of phase, and list that as the FLA of the panel.
Main disconnect/breaker sizing is based on 80% of the highest FLA per phase, which leads to some angry installers, because the FLA is larger than the Main breaker size.
Thanks,
JB
UL508a Section 49.2 (Supply Ratings)
The full-load ampere rating of the panel shall, at a minumum, include the sum of the ampere ratings of all loads that are able to be operated simultaneously plus the primary ampere rating of all control transformers connected to the input voltage.
How does this apply to multi-phase systems? Currently, we just total up all the loads, regardless of phase, and list that as the FLA of the panel.
Main disconnect/breaker sizing is based on 80% of the highest FLA per phase, which leads to some angry installers, because the FLA is larger than the Main breaker size.