Trying to determine if the MDP is overloaded.
The Main Bus has a 120/208V/3P 1000A Main Breaker.
There is also a sign on the right that says "Main Bus Modified to 1200 AMP Capacity...", which is showing 120/208V/3P 200A Breaker.
Please refer to the photo attached of the MDP.
I took the breaker size and took 80% of the breaker.
How can you calculate the MDP load without taking a meter to it for 30 days.
I attached my panel schedule for your reference.
 

Attachments

  • Mike Electrical Schedule.pdf
    33.7 KB · Views: 10
  • DSC_2990-min.JPG
    DSC_2990-min.JPG
    1.7 MB · Views: 17
Trying to determine if the MDP is overloaded.
The Main Bus has a 120/208V/3P 1000A Main Breaker.
There is also a sign on the right that says "Main Bus Modified to 1200 AMP Capacity...", which is showing 120/208V/3P 200A Breaker.
Please refer to the photo attached of the MDP.
I took the breaker size and took 80% of the breaker.
How can you calculate the MDP load without taking a meter to it for 30 days.
I attached my panel schedule for your reference.

You can check the design documents.
 
Honestly, I have never understood why people put the loads on a panel schedule. It is pretty much worthless information (except at the design stage of course). I would get the demand data from utility and go from there.

It’s not worthless. How else are you going to document the load? The problem is people don’t maintain their records every time something is added or removed. With up to date schedules, the OP wouldn’t have an issue.
 
It’s not worthless. How else are you going to document the load? The problem is people don’t maintain their records every time something is added or removed. With up to date schedules, the OP wouldn’t have an issue.
I get away from NEC calcs as soon as possible. Typically for me this after the plan review and inspection process. Except for some specific applications, NEC calc values are almost meaningless. I prefer to go off of my experience, actual load readings, or demands data.
 
I get away from NEC calcs as soon as possible. Typically for me this after the plan review and inspection process. Except for some specific applications, NEC calc values are almost meaningless. I prefer to go off of my experience, actual load readings, or demands data.

What jurisdiction are you in? Permitting and inspection is almost always required. Especially for anything above 800-amperes.
 