I know from 220.14(I) that receptacle outlets are calculated at 180VA per each receptacle yoke. But what if you know that a particular appliance or piece of equipment that will be plugged in is a high-wattage device?
For example, let's say we have a kitchenette in an office building. There is a kitchen counter and we want multiple general use outlets available on that counter. But we know there will be a microwave placed somewhere on that counter, a coffee brewer, and an induction cooker. None of these appliances will be built in, so I don't see how they can have dedicated circuits (the appliances could be moved around in the future). But, for the sake of this example, let's say that each appliance draws 15A and is rated at 1,800W. Clearly, they can't all be on a single 20A circuit. Yet it's very likely that two or more devices could be in use at the same time.
1. How do we account for these anticipated loads in the load calcs if these are not on dedicated circuits?
2. How would you design the branch circuits serving this counter that allows flexibility in usage (the appliances listed above being moved around plus the addition of future loads, like a juicer or espresso machine) without the risk of a circuit being overloaded and having nuisance trips?
For example, let's say we have a kitchenette in an office building. There is a kitchen counter and we want multiple general use outlets available on that counter. But we know there will be a microwave placed somewhere on that counter, a coffee brewer, and an induction cooker. None of these appliances will be built in, so I don't see how they can have dedicated circuits (the appliances could be moved around in the future). But, for the sake of this example, let's say that each appliance draws 15A and is rated at 1,800W. Clearly, they can't all be on a single 20A circuit. Yet it's very likely that two or more devices could be in use at the same time.
1. How do we account for these anticipated loads in the load calcs if these are not on dedicated circuits?
2. How would you design the branch circuits serving this counter that allows flexibility in usage (the appliances listed above being moved around plus the addition of future loads, like a juicer or espresso machine) without the risk of a circuit being overloaded and having nuisance trips?