Leo1
Member
- Location
- Los Alamos, NM
Any suggestions on how to feed a small 5kVA 120/240VAC transformer from a 400AMP, 480VAC, 3-phase fused safety disconnect switch NEC compliant and economically? Placing a large junction box or wireway below the fused safety disconnect switch with terminal blocks for continuation of 400AMP conductors to their load and tapping smaller conductors to feed the small transformer(per 240.21) is a solution. However, the fused safety disconnect switch is approx. 3' high and the junction box to accommodate 600kcmil conductors with terminal blocks is also near 3' high which is placing the top of the fused safety disconnect switch near 7' high to keep the junction box cover off the ground a few inches not to mention the cost of the large junction box, terminals and labor. Getting an extra set of lugs in the fused safety disconnect switch is not doable I have been told.