newschool
Member
- Location
- Wailuku Hi
Hello all this is in reference to the 2008 NEC 450.5
"Zig-zag connected transformers shall not be installed on the load side of any system grounding connection..."
The service is a 480V 3ph/4W and we are extending a 3ph/3w feeder to a photovoltaic inverter. At the inverter we are providing a grounding transformer in the form of a zig-zag autotransformer to comply with local utility requirements.
So I understand that we are not to connect to the load side of any system grounding but can I assume that running a 3ph/3w feeder doesn't apply here? If this is the case then do we create a new system ground at the grounding transformer and tie to a new grounding electrode system? I have read else where that the neutral point floats but then what do we do with the equipment grounding?
Thanks in advance.
"Zig-zag connected transformers shall not be installed on the load side of any system grounding connection..."
The service is a 480V 3ph/4W and we are extending a 3ph/3w feeder to a photovoltaic inverter. At the inverter we are providing a grounding transformer in the form of a zig-zag autotransformer to comply with local utility requirements.
So I understand that we are not to connect to the load side of any system grounding but can I assume that running a 3ph/3w feeder doesn't apply here? If this is the case then do we create a new system ground at the grounding transformer and tie to a new grounding electrode system? I have read else where that the neutral point floats but then what do we do with the equipment grounding?