230.55 explicitly states "appliances individually rated in excess of 1 3/4 kW shall be permitted to be calculated in accordance with Table 230.55"
Rare in the field I expect, but I have class homework range calcs that include ranges of 1 kW.
Column 1 of Table 230.55 at "Less than 3 1/2 kW Rating" would seem to include 1kW, however the heading of the table, clearly again, "Demand Factors and Loads for Electric Ranges...and Cooking Appliances over 1 3/4 kW"
My guess is nameplate, but need a bonafide code reference to verify as this is exam prep. Anyone?
thanks,
-Tim
[ October 29, 2005, 12:07 PM: Message edited by: TimWA ]
Rare in the field I expect, but I have class homework range calcs that include ranges of 1 kW.
Column 1 of Table 230.55 at "Less than 3 1/2 kW Rating" would seem to include 1kW, however the heading of the table, clearly again, "Demand Factors and Loads for Electric Ranges...and Cooking Appliances over 1 3/4 kW"
My guess is nameplate, but need a bonafide code reference to verify as this is exam prep. Anyone?
thanks,
-Tim
[ October 29, 2005, 12:07 PM: Message edited by: TimWA ]