Here is a picture where someone tried to keep a breaker from tripping, but due to the breaker design, this won't work.
A perhaps unintended consequence of locking a breaker in the on position is that it cannot be reset after a trip without the key or tool required to unlock it.Locking breakers in the ON position is required by some sections of the NEC although I don't think that this is how they intended for it to be done.![]()
A perhaps unintended consequence of locking a breaker in the on position is that it cannot be reset after a trip without the key or tool required to unlock it.
Sent from my XT1585 using Tapatalk
cannot be reset after a trip without the key or tool required to unlock it.
Kleins?
That looks like a lock off to me.GE THQB breaker lock on most other companies are the same design.
![]()
Square D QO breaker breaker lock on
![]()
That looks like a lock off to me.![]()
In most cases, just fingers. Most of the breaker lock on devices slip on the breaker handle and are held by friction.
Square D uses a set screw on the side that takes a small screwdriver.
Thank you, I will be sending the award, along with a plaque and medal out soon.You have just won the kwired award for stating the obvious.![]()
Thank you, I will be sending the award, along with a plaque and medal out soon.
I believe it says right in the Square D catalog that the model you posted a picture of is for locking a breaker in on or off position.
I agree with your first sentence. Usefulness for lock off is very limited if you factor in NEC or OSHA lock off requirements.
Yes it does, but that model will not meet the NEC or OSHA for locking things off so I do not really see the usefulness of it.:?
It is barely useful as a lock on. Its more like a visual hint that the breaker should not be shut off.
Only somewhat agree with the rest, it is a visual hint I guess, but also is a mechanical inhibit - you are not turning that breaker off without damaging something or removing the locking device, but overload, short circuits, ground faults will still trip the breaker, you will need to remove the lock device to reset the breaker.
They come in handy in panels that breakers are also used as lighting switches, or any other place where people seem to frequently be in the panel to prevent accidental turn off of selected circuits you want to make harder to turn off.
I suppose the GE model will, I never been around one.:slaphead::slaphead:
The reason I question the usefulness of the stamped spring steel design is that they fall right off.
I suppose the GE model will, I never been around one.
The QO model has a set screw and does not come off very easily without loosening that screw, I have seen many of those.
Here is a picture where someone tried to keep a breaker from tripping, but due to the breaker design, this won't work.