Disconnect cable at both ends... including the shield. Test insulation resistance between each conductor, each conductor and shield, each conductor and ground, and shield and ground...Hello,
I have a 1 pair, 2 conductor #16 cable with shield used for instrument control (4-20mA Hart). Instrument is connected in the field and powered.
How do I meg each conductor to make sure insulation of the conductor is good?
Thank you very much
Disconnect cable at both ends... including the shield. Test insulation resistance between each conductor, each conductor and shield, each conductor and ground, and shield and ground...
Test is for insulation degradation... so you test insulation resistance between every conductor combination including 'ground' as an additional conductor [n!-(n-1)! tests, where n is the total number of conductors plus ground]. In your case, it is desired for the shield to be grounded at only one point, to prevent circulating currents, especially those that cause signal interference. You must test insulation between shield and ground to verify the intentional connection to ground is the only connection to ground.Thank you Smart $
I am still a bit new to megging. But why test the insulation resistance between each conductor, each conductor and shield, each conductor and ground, and shield and ground?
Also, why test shield and ground?
Thanks
Thank you Smart $
I am still a bit new to megging. But why test the insulation resistance between each conductor, each conductor and shield, each conductor and ground, and shield and ground?
Also, why test shield and ground?
Thanks
Test is for insulation degradation... so you test insulation resistance between every conductor combination including 'ground' as an additional conductor [n!-(n-1)! tests, where n is the total number of conductors plus ground]. In your case, it is desired for the shield to be grounded at only one point, to prevent circulating currents, especially those that cause signal interference. You must test insulation between shield and ground to verify the intentional connection to ground is the only connection to ground.
Be careful what voltage level you use for the test. a lot of instrument cable is not rated for much in the way of voltage.
Yes... megohms preferred, but hundreds of kilohms may be acceptable.Thank you,
So we are looking for lots (megaohms) between the conductors to make sure no chance for shorting the conductors?
Which ground do I use during the test? Do I use the ground at the control system where the 2 conductors and shield will terminate at? And the ground at the instrument in the field?
Thank you
I think testing at 500V is your only option with a standard megger.Thank you,
I will confirm the voltage rating for the conductors and set the test voltage to whatever it is rated for. So if the rating is 500V, I will set test voltage to 500V. But I wonder if other instrument cable in the tray will be effected by the 500V:??
Thanks
500V DC voltage test is typically acceptable for 300V-rated insulation.Is your cable TC-type or standard CMP? Regular cable for instrument use is usually listed to only 300V.
Is your cable TC-type or standard CMP? Regular cable for instrument use is usually listed to only 300V.
Thank you Smart $,Use ground at power-source end.
A cabinet ground bus is okay. Advise against using a ground terminal on an I/O card. You will likely be using a substantially higher voltage than the I/O cards are designed for.Thank you Smart $,
I will use the ground bus back at the control systems I/O card where the shield is normally connected.
Thanks
A cabinet ground bus is okay. Advise against using a ground terminal on an I/O card. You will likely be using a substantially higher voltage than the I/O cards are designed for.
Shouldn't as long as it is solidly connected to the power supply grounding conductor.Thank you Smart $,
The cabinet ground bus has other sheilds from other devices wires attached as well. Will the high voltages effect does devices while megging the cable?
Shouldn't as long as it is solidly connected to the power supply grounding conductor.
I was just at www.biddlemegger.com and came across TDR meters...from reading the specs on it seems to be prefect for your needs to check out the integrity of the cable.
Go check it out! JMHO.
Shouldn't as long as it is solidly connected to the power supply grounding conductor.