I've worked on many renovations from retail to office space jobs (NYC mostly) but a comment I just got on a recent job is making my head explode
Basically he's saying regardless of me knowing the exact wattage of every lighting fixture, I should be using table 220.12 to determine my lighting demand.
Besides that seeming just dumb on its face (why would I use a generic number when I know the what the largest lighting load would be?), these loads wouldn't even meet the Energy Code without a lot of exceptions being applied (which I guess wouldn't even count because that wouldn't be "general lighting").
Basically he's saying regardless of me knowing the exact wattage of every lighting fixture, I should be using table 220.12 to determine my lighting demand.
Besides that seeming just dumb on its face (why would I use a generic number when I know the what the largest lighting load would be?), these loads wouldn't even meet the Energy Code without a lot of exceptions being applied (which I guess wouldn't even count because that wouldn't be "general lighting").