How do I determine the size of the RTU breaker and FLA from the nameplate
Do I take the MCA and multiply it by 1.25 or take the largest load and multiply it by 1.25
I would typical use the max fuse size of 25 per the nameplate and take the MCA of 21.
But I see the Compr A and B only shows a RLA and the fan loads shows FLA.
When I add the RLA and FLA amp together I get 17.75 AMP.
Can you add RLA and FLA together?
Do I take the MCA and multiply it by 1.25 or take the largest load and multiply it by 1.25
I would typical use the max fuse size of 25 per the nameplate and take the MCA of 21.
But I see the Compr A and B only shows a RLA and the fan loads shows FLA.
When I add the RLA and FLA amp together I get 17.75 AMP.
Can you add RLA and FLA together?