I've attached a sample electric bill for one month (have 12 months total of usage)
I'm trying to determine the current usage because the owner is adding lots of new load and I want to be able to determine existing capacity vs. new required capacity.
Do I just take where it says Demand-kW and that's how much consumption the user has? Or do I do something with the kWh row?
Better pic here: https://cdn1.imggmi.com/uploads/2019/7/16/6092a80c8abce0bdd58fd04470ca5222-full.png
Thank you!
Jraef
Moderator, OTD
Electrical Engineer
You cannot determine service capacity from a utility bill. From their standpoint, 63,588kWH could be 1kW for an hour, followed by 63,587kW for an hour, with nothing else all month, it all looks the same at the end of the month.
The kW and kVA demand values are just the peak amount used during sliding time slot called the "demand window", but they don't say here whether it is 15 min., 20 min,. or 30 min., all of which are common in different areas. But again, that is the AVERAGE across a single demand window, it means nothing with regard to what they have available.
Can't you just ask the utility for the size of the service?
Designer69
Thanks Jraef. I'm basically trying to determine the margin (available capacity still left) in the existing system and how much more it can handle.
I can figure out how big their existing service is. Let's say it is 480V/3Ph, 200A, well I know I'm using 138A (per the demand-kw on the electric bill) and I would have another 62A available. Or I would need to upsize the service.
The NEC allows this method right?
drktmplr12
South Florida
Electrical Engineer
Not that I am aware, see 220.87
looks like the maximum demand here might be 127.6 kVA, but it isn't clear to me if that is for the past month for past year. assuming it is for the year, multiply by 1.25 per 220.87 then add the new continuous and non-continuous loads. that will determine your minimum feeder size for the new installation.
jaggedben