Prototype1
Member
- Location
- Kansas City
- Occupation
- Noob EE
1: I went to Article 430.120 – FLC – 65 A * 1.25 = 81.25 A
2: Table 310.16, look at 75deg C Copper- the AWG at 81.25 Amp is AWG 4.
3: On diagram: The breaker is 150 AF; Table 250.122: 200 is closet to 150: so, AWG 6 G
4: Ch-9 Table-5: At AWG 4- (XHHW)- 0.0814 * 3 = 0.2442
5: Ch-9 Table-5: At AWG 6- (XHHW) – 0.0590 = 0.0590
6: 0.2442 + 0.0590 = 0.3032
7: Ch-9 Table 1: Over 2 conductor: 40%: 0.3032 / 0.4 = 0.758
8: Ch-9 Table 4: RMC article 352-353 – value close to 0.758 (over 2 wires 40%) is 0.794 and
Trade size is 1½, Ground - #6G, #4 AWG
For (50 HP) 65 A.
This is the steps I took to find the ground, conductor, and conduit size using NEC code book 2023. Now, I want to know how to size the generator and breaker. Please help.
I am still new to this NEC code book and single line diagram. I am still confuse on what steps to take.
2: Table 310.16, look at 75deg C Copper- the AWG at 81.25 Amp is AWG 4.
3: On diagram: The breaker is 150 AF; Table 250.122: 200 is closet to 150: so, AWG 6 G
4: Ch-9 Table-5: At AWG 4- (XHHW)- 0.0814 * 3 = 0.2442
5: Ch-9 Table-5: At AWG 6- (XHHW) – 0.0590 = 0.0590
6: 0.2442 + 0.0590 = 0.3032
7: Ch-9 Table 1: Over 2 conductor: 40%: 0.3032 / 0.4 = 0.758
8: Ch-9 Table 4: RMC article 352-353 – value close to 0.758 (over 2 wires 40%) is 0.794 and
Trade size is 1½, Ground - #6G, #4 AWG
For (50 HP) 65 A.
This is the steps I took to find the ground, conductor, and conduit size using NEC code book 2023. Now, I want to know how to size the generator and breaker. Please help.
I am still new to this NEC code book and single line diagram. I am still confuse on what steps to take.