How to Size Conductors, breakers, conduit, meter?

Status
Not open for further replies.

Prototype1

Member
Location
Kansas City
Occupation
Noob EE
Hey guys, I am trying to size the breaker, conductor, conduit and meter. From attached photo #2, I have 50 HP (65A), and 250 HP (302A).

What steps I need to take to find the size of breaker? Conductor? conduit, and meter?

This is my thought process: to how to size it:
1: I went to Article 430.120 – FLC – 65 A * 1.25 = 81.25
2: Table 310.16, look at 75deg C Copper- the AWG at 81.25 Amp is AWG 4.
3: For the breaker; Table 250.122:
4: Ch-9 Table-5: (XHHW) Wire (AWG 4) * 3 = Ans
5: Ch-9 Table- (XHHW) AWG Ground
6: Wire + GND= Answer
7: Ch-9 Table 1: Over 2 conductor: 40%: step 6 answer/ 0.4 =
8: Ch-9 Table 4: RMC article 352-353 –
value close to step 7 (over 2 wires 40%) to get trade size is


Please give your insight. It will be great if you wrote out steps. It will give me more clarity.

Thank you,

Fellow electrical guy.
 

Attachments

  • 1.jpeg
    1.jpeg
    138.6 KB · Views: 17
  • 2.jpeg
    2.jpeg
    76.3 KB · Views: 16
This is my thought process: to how to size it:
1: I went to Article 430.120 – FLC – 65 A * 1.25 = 81.25
2: Table 310.16, look at 75deg C Copper- the AWG at 81.25 Amp is AWG 4.
3: For the breaker; Table 250.122:
4: Ch-9 Table-5: (XHHW) Wire (AWG 4) * 3 = Ans
5: Ch-9 Table- (XHHW) AWG Ground
6: Wire + GND= Answer
7: Ch-9 Table 1: Over 2 conductor: 40%: step 6 answer/ 0.4 =
8: Ch-9 Table 4: RMC article 352-353 –
value close to step 7 (over 2 wires 40%) to get trade size is
Can you explain with some more detail what you're looking for in 4-9? Are you trying to find the size of the RMC raceway?
 
You mentioned 430.120.. Is a variable speed drive involved ?
If so, are you sizing conductrs/OCP to the load or the drive supply ?
 
Can you explain with some more detail what you're looking for in 4-9? Are you trying to find the size of the RMC raceway?
diagram from my post. So, here is what I did:
Branch circuit conductors:
50 HP [FLC= 65A, 65A*125% = 81.25A got Conductor size AWG 4]
250 HP [FLC= 302A, 302A*125% = 377.5A got Conductor size AWG 500MCM table 310.16(75 ,Copper)].

Branch circuit overcurrent device: NEC 430.52(C)(1)
For 50 HP - I am doing 65 A * 250% = 162.5 Amp breaker. But from ugly book, for 50 HP size breaker-150A. For 250 HP - 302 * 250% = 755 A. But the size breaker is 500 A. Should I not go up and standard size of breaker?

Feeder Connectors:
From 250 HP - (125% * 3025A) + 65 (FLC) = 442.5. AWG-700 MCM/ 460A (table 310.16(75, copper column))

Feeder OCD:
250 HP - 500 fuse (302 (FLC)
50 HP - 200 Fuse (65 FLC) ( I got 200 A from ugly book page. 42) But for 50 HP size breaker on page: 40 it is 150 A breaker.

So largest OCD: 500 fuse +65 (FLC) - 565 Amp and that will be 600 Amp (OCD) - table 310.16 AWG 350 MCM/ 310 A (running 2 in parallel).
 
diagram from my post. So, here is what I did:
Branch circuit conductors:
50 HP [FLC= 65A, 65A*125% = 81.25A got Conductor size AWG 4]
250 HP [FLC= 302A, 302A*125% = 377.5A got Conductor size AWG 500MCM table 310.16(75 ,Copper)].

Branch circuit overcurrent device: NEC 430.52(C)(1)
For 50 HP - I am doing 65 A * 250% = 162.5 Amp breaker. But from ugly book, for 50 HP size breaker-150A. For 250 HP - 302 * 250% = 755 A. But the size breaker is 500 A. Should I not go up and standard size of breaker?

Feeder Connectors:
From 250 HP - (125% * 3025A) + 65 (FLC) = 442.5. AWG-700 MCM/ 460A (table 310.16(75, copper column))

Feeder OCD:
250 HP - 500 fuse (302 (FLC)
50 HP - 200 Fuse (65 FLC) ( I got 200 A from ugly book page. 42) But for 50 HP size breaker on page: 40 it is 150 A breaker.

So largest OCD: 500 fuse +65 (FLC) - 565 Amp and that will be 600 Amp (OCD) - table 310.16 AWG 350 MCM/ 310 A (running 2 in parallel).
You are doing too many things at once. So let's take the first couple steps and then you can do the next one from there. Amperages from table 420.147-150. If your first step is right, your second step is wrong. Overcurrent protection isn't FLC*1.25*250% It is FLC*250%. conductor size is *1.25.
 
You are doing too many things at once. So let's take the first couple steps and then you can do the next one from there. Amperages from table 420.147-150. If your first step is right, your second step is wrong. Overcurrent protection isn't FLC*1.25*250% It is FLC*250%. conductor size is *1.25.
I was following Motor branch circuit and feeder example from ugly book page: 42.
 
Update: I got the conductor, conduit, ground size and know how to size them now (Also breaker with help of ugly book) But got still have no idea how to size a breaker properly (still suck at it).
 
Update: I got the conductor, conduit, ground size and know how to size them now (Also breaker with help of ugly book) But got still have no idea how to size a breaker properly (still suck at it).
one motor. get the FLA from tables 430.147-430.150. The go to 430.52 select the proper column or line and do the math. That simple.
 
one motor. get the FLA from tables 430.147-430.150. The go to 430.52 select the proper column or line and do the math. That simple.
more than 1 motor (feeder) 430.62... rating of largest GFSC device (from above) + FLC of other motors or loads
 