Hi All, this is my first post.
I've asked this question on another forum, but was told to post my question here.
I'm working on a project where I need to size a 460V chiller from a switchboard that is rated at 208V. I'll need to provide a step up transformer, but there's a few items that I'd like to clarify. The chiller has the following characteristics at 460V:
According to the Canadian Electrical Code, I will need to account for inrush current at no more than 250% for the overcurrent Protection. Therefore, 1073A * 2.5 = 2682A. My question is, the cutsheets says there is 0 in rush. Can I get away with using a 1600A breaker that has an adjustable trip setting?
Note that my transformer is sized at 450KVA. For my wire size, I have sized it based on the MCA but at 208V. Should I be sizing it from the transformer? And for my own knowledge, can transformers handle inrush current from motors, or do you have to typically size it to account for it?
Thanks
I've asked this question on another forum, but was told to post my question here.
I'm working on a project where I need to size a 460V chiller from a switchboard that is rated at 208V. I'll need to provide a step up transformer, but there's a few items that I'd like to clarify. The chiller has the following characteristics at 460V:
- Motor FLA = 551A
- LRA = 3500A
- Inrush Amps = 0
- MCA = 690A
- Max Breaker = 1200A
- KW = 386.6kW
According to the Canadian Electrical Code, I will need to account for inrush current at no more than 250% for the overcurrent Protection. Therefore, 1073A * 2.5 = 2682A. My question is, the cutsheets says there is 0 in rush. Can I get away with using a 1600A breaker that has an adjustable trip setting?
Note that my transformer is sized at 450KVA. For my wire size, I have sized it based on the MCA but at 208V. Should I be sizing it from the transformer? And for my own knowledge, can transformers handle inrush current from motors, or do you have to typically size it to account for it?