Scenario: A transformer with a secondary voltage of 240/120V is supplying a load of 200 A per phase.
Question: What should be size of the 1) neutral and 2) ground wire?
My thoughts are these.
1) The neutral wire of the transformer should be rated to carry sum of the two phase current that is 400A and the size should be 600 kcmil. is common for both phases then the neutral will carry sum of the current of 2 phases, that is 400 amp ( but I don?t recall seeing any neutral that double the size of phase)
2) For ground wire, I choose the size this way: the current carrying conductor size for 200A is 3/0. From table 250.66 the ground conductor size is #4 AWG
I think I am wrong in both, buy why?
Question: What should be size of the 1) neutral and 2) ground wire?
My thoughts are these.
1) The neutral wire of the transformer should be rated to carry sum of the two phase current that is 400A and the size should be 600 kcmil. is common for both phases then the neutral will carry sum of the current of 2 phases, that is 400 amp ( but I don?t recall seeing any neutral that double the size of phase)
2) For ground wire, I choose the size this way: the current carrying conductor size for 200A is 3/0. From table 250.66 the ground conductor size is #4 AWG
I think I am wrong in both, buy why?