How to tap load side of 400A breaker for a Type 1 or Type 2 SPD?

Status
Not open for further replies.

natfuelbill

Senior Member
What wiring methods have you used to connect the SPD spagetti-size wires to the breaker terminals or feeder conductors?

I'm scratching my head to understand the best (NEC compliant) method.

Most methods I have seen just appear to have had the SPD wires inserted into the loosened termination next to the conductor...
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Although I have seen many connected as you described, IMO, it is a NEC violation unless the lug is properly rated for such a connection.
I may be incorrect, but my memory is that the Type 2SPDs I have seen have a manufacturer OCP requirement far less than 400 amps.
 