130219-1723 EST
harsha1972:
I don't understand your 6 ohm measurement or the calculations.
#12 copper wire has a resistance of about 1.6 ohms per 1000 ft. If the conduit is good, then I would expect the resistance of the conduit to be less than a #12 copper wire. Even #3 aluminum is less than #12 copper. Thus, a measurement of 6 ohms for the sum of the neutral and conduit makes no sense.
For low resistance measurements you can not use an ordinary DC ohmmeter.
Essentially you need to do a four terminal resistance measurement. This means you pass a known current thru the resistance, then measure the voltage drop between two points. These points are directly on the resistance such that the voltage drop across the interface at the current injection points is not seen by the voltage measurement.
Run a long wire from the main neutral bus to near the far end of your conduit. This could be #22 insulated wire. It will be one test lead to your high impedance sensitive voltmeter. A Fluke 27 would work. Remove any power to the circuits in this conduit.
Measure the voltage between the far conduit end and the long test lead. Should be 0.
Use a 5 to 10 V isolation transformer with 20 A capability. Control the transformer input voltage with a Variac. Start at zero V. Disable power to any circuits that use the neutral. Connect one side of the transformer secondary to the neutral. Connect the other secondary lead to the conduit. Adjust the Variac to obtain near 20 A thru the conduit.
Measure the voltage over the length of the conduit. Should be small. The conduit resistance is the measured voltage divided by the injected current.
.