180316-0730 EDT
jjhoward:
I don't think it should be too difficult to troubleshoot your voltage drop.
Test equipment needed ---
1. Two 120 V 1500 W portable space heaters. Would like equal current at sane voltage. Or use some 240 heating element. Goal is to get around a 10 A or higher load at 240 V.
2. Fluke 27 or equivalent. 87 if you want finer resolution. RMS or average reading, not a big concern.
3. Hall type or standard current transformer clamp-on current probe.
4. A long test lead, somewhat over your 350 ft. This could be #30 wire, but there would be no reason to go this small. Probably #16 or #14 so you can reuse it. I don't know if excess coiled on the spool will be a problem. Depends upon stray magnetic fields. The error from the measuring 1 turn loop of the conductor being tested and your stretched out long probe wire is probably not important.
5. Some way to directly probe conductors.
6. Possibly an extra person or so.
7. Some radio communication.
First test is to determine source impedance looking back at the power company.
Apply a 10 A or greater load change on the power company 240 V lines. Measure the load change (current), great accuracy is not required. You can probably live with 10%, but 1% would be better. Put your voltmeter probes directly on the conductors that come from the power company. Possibly this will be in the main panel. Contact the wires directly. Don't just measure on the terminating lugs. This is a 240 V measurement. This should be on the power company side of wherever the PV system connects.
Z utility source = delta V / delta I. Z utility source is everything from the point where you make the voltage change measurement back to power company generators, but mostly starts at the pole transformer. I would hope this Z is less than about 0.02 ohm, but it may not be. 100 A and 0.02 ohm is 2 V. Short circuit current about 12,000 A.
Second you connect your long wire probe directly to the wire from one side of the PV inverter, and to your voltage testing meter. The meter and its other probe will be taken to various test points. Note: this is the measurement of a small voltage drop along your conductor(s), not a change in supply voltage.
These tests to various points are best done by shutting down the PV system and using your load resistor at the PV end. Any major problem point should be obvious, otherwise you have a distributed problem.
You are only measuring 1/2 of the loop impedance this way, and thus both sides of the circuit must be looked at.
The load resistor method is easier to work with because there are no big variations such as may come from a varying PV system.
After you find and correct your problems, then remove the test load resistor, and do any required tests with the PV system as the source.
Note that breakers have substantial voltage drop.