We have just installed 3 new pad mount 12470 Delta / 480 Wye transformers. We have no neutral load, it's all 3 phase motors. I have a ground grid we just installed, how should that tie into my transformer and should anything be tied to the neutral bar in the low side of my transformer? Right now it goes to the ground spot on the transformer and then to the first disconnect, but it seems like there is no way for any fault current to get back to the transformer.
 

Smart $

Esteemed Member
Location
Ohio
This is not a service transformer?

Do you want a grounded system? In heavy industry it is common to run systems ungrounded, especially where a trip can present a more dangerous condition than a line to ground fault. After all, one line to ground fault on an ungrounded system is not much different than the intentional ground of a grounded system. A ground detector is required, along with it being monitored and faults corrected as soon as can be safely managed.

If you want a grounded system, Dave has directed you to the appropriate section (if not a service transformer). There are a lot of details to that section so it is difficult to cover all the possible specifics here. So read up if that's the route you want to go, and come back if you have any additional questions.

Welcome to the forum. :thumbsup:
 

rlundsrud

Senior Member
Location
chicago, il, USA
I'm only asking this as I'm curious, I understand that it isn't practical to change anything now. Wouldn't it have been better to use a Delta secondary since there are exclusively motor loads? If so, then you could corner ground the Delta secondary.

I'm hopeful that some of the other members can weigh in on this as I would like to know what is considered the convention way of doing it.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
I'm only asking this as I'm curious, I understand that it isn't practical to change anything now. Wouldn't it have been better to use a Delta secondary since there are exclusively motor loads? If so, then you could corner ground the Delta secondary.

I'm hopeful that some of the other members can weigh in on this as I would like to know what is considered the convention way of doing it.
Wye systems are more familiar and have the added advantage of reducing the voltage to ground.
 

Smart $

Esteemed Member
Location
Ohio
His handle says Mine electrician. I would not be surprised that those are their own transformers.
I would not be surprised either. But I had to ask because the grounding details are a little different (as is the section that covers such). :D
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I'm only asking this as I'm curious, I understand that it isn't practical to change anything now. Wouldn't it have been better to use a Delta secondary since there are exclusively motor loads? If so, then you could corner ground the Delta secondary.

I'm hopeful that some of the other members can weigh in on this as I would like to know what is considered the convention way of doing it.

There are a number of reasons why a Y system would be better than a delta (even when there are only line to line loads). Among them, the phase to ground voltage is the same as line to line in a corner grounded system and thus requires equipment rated for this. In this day and age, corner grounded delta rated equipment such as panelboards, etc. is becoming less common. Also much load equipment these days, such as VFDs are not suitable for use in a corner grounded systems.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
There are a number of reasons why a Y system would be better than a delta (even when there are only line to line loads). Among them, the phase to ground voltage is the same as line to line in a corner grounded system and thus requires equipment rated for this. In this day and age, corner grounded delta rated equipment such as panelboards, etc. is becoming less common. Also much load equipment these days, such as VFDs are not suitable for use in a corner grounded systems.
The NEC also specifically instructs us to consider the effective phase to ground voltage in an ungrounded system to be equal to the line to line voltage. That will also affect what equipment you can use.
 

Smart $

Esteemed Member
Location
Ohio
There are a number of reasons why a Y system would be better than a delta (even when there are only line to line loads). Among them, the phase to ground voltage is the same as line to line in a corner grounded system and thus requires equipment rated for this. In this day and age, corner grounded delta rated equipment such as panelboards, etc. is becoming less common. Also much load equipment these days, such as VFDs are not suitable for use in a corner grounded systems.
Given the same 3Ø voltage as a corner-grounded delta, a wye system will have 57.7% (1/√3) line to ground voltage.
 