teh_engineer
Member
- Location
- Baltimore, MD
A small service is being upgraded from 150A to 200A. There is a main distribution panel that is fairly new (probably within last 5 years) that is rated for 225A with a 150A main breaker. However, at some point after the panel installation, the client installed a data rack in front of the panel within the panel's working clearance that can't really be moved.
If the main breaker is upgraded to 200A without otherwise modifying the rest of the panel, would it violate the NEC, as the working clearance is partially obstructed by a data rack? There is probably 30" in front of the panel, so the panel door can still open. Given the tightness of the electrical room and adjacent rooms (including exterior), relocating or providing a new panel is unfeasible.
I ascribe to the "you touch it, you own it" ethos, but I don't seem to be able to find the actual code definitely stating thus.
If the main breaker is upgraded to 200A without otherwise modifying the rest of the panel, would it violate the NEC, as the working clearance is partially obstructed by a data rack? There is probably 30" in front of the panel, so the panel door can still open. Given the tightness of the electrical room and adjacent rooms (including exterior), relocating or providing a new panel is unfeasible.
I ascribe to the "you touch it, you own it" ethos, but I don't seem to be able to find the actual code definitely stating thus.