Hello, 
I am using this table correct.
I have a 1kVA transformer and need to calculate OPCD size.
Data:
480V 3 phase to 120V 1 phase transformer
8 amp load for secondary side.
1. I calculate 3.5amp OPCD size. 1.67 x (1000/480) = 3.479amp. Is this correct?
2. How do i determine to use OPCD on primary and secondary?
3. Do I need a fuse on the secondary side to protect the conductors?
Thank you.
	
		
			
		
		
	
				