Most inspectors would turn to Article 680, I suggest you do to.Originally posted by jamal:
how to wire an indoor jacuzzi, dose it require disconnect switch?
thank you
Well want to talk about an open ended question here is one.Originally posted by jamal:
thank you
NoOriginally posted by jamal:
In the master bed room
Afternoon pierre,Originally posted by pierre:
a means for disconnecting the jacuzzi (hydro massage tub) will be required. See 422.30 & 90.3
I doubt he was pulling our chain.Originally posted by jwelectric:
I do believe that you had me hooked. With all my years of experience I fell for one of the biggest traps there is for article 680.
Congratulations for a job well done.
I think that 90.3 tells me that chapter six will supplement or modify chapters one through four.Originally posted by pierre:
Now I jump over to section 680.70 and here I see680.12 Maintenance Disconnecting Means.
One or more means to disconnect all ungrounded conductors shall be provided for all utilization equipment other than lighting. Each means shall be readily accessible and within sight from its equipment.
Let?s rethink this 422.30 rule, okay I have rethought it and I understand now that this disconnect is NOT required.680.70 General.
Hydromassage bathtubs as defined in 680.2 shall comply with Part VII of this article. They shall not be required to comply with other parts of this article.