We were finishing the final tie in of about 2000' of interconnected lighting counduit and boxes, conduit ranging in size from 1/2" to 1". Conduit is supported via tapcons and sammies to the poured concrete ceiling. When the feeder pipe running from the house panel to the first jb touched the metal components, it lightly sparked.
It sparked multiple times, ruling out static discharge.
The neutral and ground are bonded via bus jumper at the terminal cabinet, before the main switchboard.
The ground jumper between the terminal cabinet, passing through the CT cabinet, into the house panel was sized and torqued correctly.
Two 5/8" copper clad ground rods were driven seven feet apart, with a 3/0 CU wire running from the main grounding bus continuously through the first, to the second rod. All terminations were torqued correctly.
The 3/0 grounding conductor bonding the building rebar was installed and terminated on the main grounding bus.
The main water bonding has yet to be done.
The complete load on the building is currently about 160A, 3 phase 120/208.
It sparked multiple times, ruling out static discharge.
The neutral and ground are bonded via bus jumper at the terminal cabinet, before the main switchboard.
The ground jumper between the terminal cabinet, passing through the CT cabinet, into the house panel was sized and torqued correctly.
Two 5/8" copper clad ground rods were driven seven feet apart, with a 3/0 CU wire running from the main grounding bus continuously through the first, to the second rod. All terminations were torqued correctly.
The 3/0 grounding conductor bonding the building rebar was installed and terminated on the main grounding bus.
The main water bonding has yet to be done.
The complete load on the building is currently about 160A, 3 phase 120/208.