I run into situations like this occasionally.
Went to a machine shop to look at an existing electrical situation with an old, old, old Air Con. It is (was) being fed by a 3P 100A breaker. Couldn't read the MCA because it is so old.
Panelboard feeding this is a SqD QO rated 200A and being fed by a 225A breaker at the 1300A main section. Told the A/C manufacturer rep that the new unit should stick to 100A maybe 125A. He comes back with a MCA of 165A (3 phase.) So, I told them that they would have to get an engineer to give his blessings since there is considerable amount of other equipment connected to this panel, including this load. They were a little put out that I wouldn't sprinkle holy water on it and say they were good.
I feel I am right because I am not going to take the risk. Heck , I don't want to take that risk. Just want to hear some reassurance or critique from the engineers (and any one else, too) along with some pointers or ideas as to why an EE would be a good person to consult with situations like this.
Thanks!
Went to a machine shop to look at an existing electrical situation with an old, old, old Air Con. It is (was) being fed by a 3P 100A breaker. Couldn't read the MCA because it is so old.
Panelboard feeding this is a SqD QO rated 200A and being fed by a 225A breaker at the 1300A main section. Told the A/C manufacturer rep that the new unit should stick to 100A maybe 125A. He comes back with a MCA of 165A (3 phase.) So, I told them that they would have to get an engineer to give his blessings since there is considerable amount of other equipment connected to this panel, including this load. They were a little put out that I wouldn't sprinkle holy water on it and say they were good.
I feel I am right because I am not going to take the risk. Heck , I don't want to take that risk. Just want to hear some reassurance or critique from the engineers (and any one else, too) along with some pointers or ideas as to why an EE would be a good person to consult with situations like this.