Alwayslearningelec
Senior Member
- Location
- NJ
- Occupation
- Estimator
That's when the debate begins. You need to run out of the panel with EMT because they don't want any exposed cables so how far do you run the EMT? Just outside the electrical closet into the hung ceiling or do you carry the homeruns close to the area where all of your branch circuits terminate?Thanks all. I actually must use EMT so I was thinking of daisy chaining a few receptacles with common conduit and multiple circuits but thinking receptacles too close for that. Maybe FMC if allowed.
Ok, the "homeruns" is one aspect the branch is another. The job is all EMT so I was saying I don't it's doable to interconnect some of those receptacles with common EMT as they are so close together as I think you have to rise up a little bit to get into the stud opening. If you could go straight into each receptacle that could be done I suppose but then you would have to punch out the stud. Not sure that's allowed.That's when the debate begins. You need to run out of the panel with EMT because they don't want any exposed cables so how far do you run the EMT? Just outside the electrical closet into the hung ceiling or do you carry the homeruns close to the area where all of your branch circuits terminate?
You mention MC in the OP now you're saying that the entire job is EMT including the wall rough in? In that case feed the first receptacle from the HR and then link a few more together in the wall with EMT. You need to watch your box fill to see how many circuits you can pull through the first box.Ok, the "homeruns" is one aspect the branch is another. The job is all EMT so I was saying I don't it's doable to interconnect some of those receptacles with common EMT as they are so close together as I think you have to rise up a little bit to get into the stud opening. If you could go straight into each receptacle that could be done I suppose but then you would have to punch out the stud. Not sure that's allowed.
Yea sorry . But as I mentioned wouldn’t it be a problem linking receptacles so close with EMT it you may have to rise up at each stud ?You mention MC in the OP now you're saying that the entire job is EMT including the wall rough in? In that case feed the first receptacle from the HR and then link a few more together in the wall with EMT. You need to watch your box fill to see how many circuits you can pull through the first box.
What does that mean, "rise up?"I think you have to rise up a little bit to get into the stud opening.