HP change calc

Status
Not open for further replies.
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Pump DataRevised Data @:
Original60 HZ58.056.054.052.050.048.046.044.0
Rpm/dia17701711.01652.01593.01534.01475.01416.01357.01298.0
Gpm10501015.0980.0945.0910.0875.0840.0805.0770.0
Hd116108.4101.094.087.180.674.268.262.4
Equiv psi50.22846.943.840.737.734.932.129.527.0
Torque3561ft/lbs
hp100
rpm1770
Increments-2Revised
Hz6058.056.054.052.050.048.046.044.0
Rpm/dia17701711.01652.01593.01534.01475.01416.01357.01298.0
ratio29.5
Fan/Pump Power
Original RPM1770
Original Power74570
2nd RPM1711.01652.01593.01534.01475.01416.01357.01298.0
Power Rqd - KW7457067358.860628.254361.548542.343153.938179.833603.529408.2
% Change-9.67%-18.70%-27.10%-34.90%-42.13%-48.80%-54.94%-60.56%
RPM96.67%93.33%90.00%86.67%83.33%80.00%76.67%73.33%
of original KW90.33%81.30%72.90%65.10%57.87%51.20%45.06%39.44%
2nd HP reqd100100757560605040

Customer is wanting to put a vfd on an existing well that feeds two pivots. He is the new owner and will not be running both pivots at the same time. One larger than the other. Does the reduction in KW and HP required at the different HZ look right? 50HZ will deliver enough water for the smaller pivot.
 

Ingenieur

Senior Member
Location
Earth
yes

pump power ~ GPM x Head
so a ratio of new/60 Hz can be used
74570 (60 Hz power) x (new Hz gpm x hd)/(60 Hz GPM x hd)

50 Hz
74570 x (875 x 80.6)/(1050 x 116) = 43178 W or 58 HP, use 60 HP (your table 43153.9 W)
matches your chart

44 Hz
74570 x (770 x 62.4)/(1050 x 116) = 29228 W or 39 HP, use 40 HP (your table 29408.2 W)
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
yes

pump power ~ GPM x Head
so a ratio of new/60 Hz can be used
74570 (60 Hz power) x (new Hz gpm x hd)/(60 Hz GPM x hd)

50 Hz
74570 x (875 x 80.6)/(1050 x 116) = 43178 W or 58 HP, use 60 HP (your table 43153.9 W)
matches your chart

44 Hz
74570 x (770 x 62.4)/(1050 x 116) = 29228 W or 39 HP, use 40 HP (your table 29408.2 W)
Thank you.

It's the first I've tried my hand at the Power reduction portion. GPM vs HZ, I've done.
 

Besoeker

Senior Member
Location
UK
Thank you.

It's the first I've tried my hand at the Power reduction portion. GPM vs HZ, I've done.
Looks like a centrifugal pump.
There is a simpler way. Mulyiply the power by the ratioratio of the speeds cubed.

P2 = P1*(n2/n1)^3

So, for 50Hz you get P2 = 74570*(1475/1770)^3 = 43153.9

BTW, your second table staates kW.
I assume you meant W.
 

Ingenieur

Senior Member
Location
Earth
Looks like a centrifugal pump.
There is a simpler way. Mulyiply the power by the ratioratio of the speeds cubed.

P2 = P1*(n2/n1)^3

So, for 50Hz you get P2 = 74570*(1475/1770)^3 = 43153.9

BTW, your second table staates kW.
I assume you meant W.

yep
meant W
ahhh....the affinity rule :D
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Looks like a centrifugal pump.
There is a simpler way. Mulyiply the power by the ratioratio of the speeds cubed.

P2 = P1*(n2/n1)^3

So, for 50Hz you get P2 = 74570*(1475/1770)^3 = 43153.9

BTW, your second table staates kW.
I assume you meant W.
I think they tried to teach us how to simplify back in grade school. Obviously I was sick that week.

Yes, W.
 

Besoeker

Senior Member
Location
UK
I think they tried to teach us how to simplify back in grade school. Obviously I was sick that week.

Yes, W.
And obviously I can't spell ratio.........:)
Or staates...........
Or maybe it's just phat phingers..........:D

Ever so slightly more seriously, I like to try to keep things as simple as they can be. It reduces the probability of errors. Occam's razor comes to mind.
Maybe I should have asked you why you wanted to convert from HP to kW. I don't disagree with your conversions BTW. I was just curious about the why....

Another small point. You have expressed some of the calculations to six digits of resolution. That doesn't make them incorrect as calculations of course.
I'd have made the 43153.9W 43kW for example. You don't need to know it to the lat tenth of a watt. We wouldn't normally be able to measure to that degree of resolution.

Just my two pence worth.
 

Ingenieur

Senior Member
Location
Earth
I think they tried to teach us how to simplify back in grade school. Obviously I was sick that week.

Yes, W.

since the pump speed is fixed by freq/poles

new power = (new f/base f)^3 x base power
(50/60)^3 x 74570 W = 43154 W

the pimp hydraulic power is the one I'm used to
power new/power base ~ the ratio of (gpm x ft head)

no right or wrong, whatever is easier for you to wrap you noggin' around lol
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Ever so slightly more seriously, I like to try to keep things as simple as they can be. It reduces the probability of errors. Occam's razor comes to mind.
Maybe I should have asked you why you wanted to convert from HP to kW. I did not think about using HP to directly replace KW. I don't disagree with your conversions BTW. I was just curious about the why....

Another small point. You have expressed some of the calculations to six digits of resolution. That doesn't make them incorrect as calculations of course.
I'd have made the 43153.9W 43kW for example. You don't need to know it to the lat tenth of a watt. We wouldn't normally be able to measure to that degree of resolution.
I let my spreadsheet determine the resolution and was curious as to how close they would come to my Lookup table. I changed the decimal places on some, others I did not.
Just my two pence worth.

This appears to work for the few I tried.

p2=p1*(n2/n1)^3hp2=hp1*(n2/n1)^3
p175KWHP1100
rpm117701770
rpm2 14751593
p243KWHP272.9

Thank you.
 

Besoeker

Senior Member
Location
UK
This appears to work for the few I tried.

p2=p1*(n2/n1)^3hp2=hp1*(n2/n1)^3
p175KWHP1100
rpm117701770
rpm2 14751593
p243KWHP272.9

Thank you.
One ought to use rpm as you have done but for this particular motor it works with frequency also. That's because the slip is given the same value at all duty points. Normally, the slip would reduce as the load reduces.
In the grand scheme of things, it doesn't make a huge difference.
 