Why is it that HP rating is equal to KVA rating when it comes to
Short circuit calculation? Are there any exception to that practice? Thank you...
Yes, that gives you an approximation to rated current if pf times efficiciency is about 0.75 which is not unusual.It's really an approximation of the input power required to generate 1 HP at the shaft of a motor.
1 HP = 746 Watts at the shaft.
Resultant VA = 746/0.8 (typical motor pf) = 932.5 VA at the shaft.
Motor efficiency is on the order of 90%.. or for the purpose of the KVA=HP approximation = 93.25 % - which necessitates 1 kVA input power to the motor.
John M
....the FLA (calculated from 1KVA/HP or off nameplate) is NOT a good estimate of the short circuit contribution supplied by a motor. It depends on transient reactance of the motor and shouldn't be guessed at but calculated. People here with a lot more experience than I have may have a better answer but a multiple of 4X to 7X the full load current is probably a better estimate... but remember I said, don't estimate it, get some data and calculate it.