I did a prep for a hydromassage unit.
20 amp 120v. - with a switch on a wall for a timer. power>switch>tub
turns out the owner got a Kohler 240v unit with a heater
kohler underscore k1835h2
spec calls for hard wire 240v 20 amp... controls are in the unit.
(I may keep the switch location installed for future if someone rips out the kohler and sticks in a regular 120v unit, or rewire and just bring the feed to the tub area and install AC disconnect)
Evening thing is still open so it's not a problem to feed straight to tub and lose the wall switch.
The unit specs say the motor is 11 amps and the heater is 1500w..
I'm considering the ac "cheapo" water proof 30 amp pull out non fused disconnect. BUT ..
looking at 430.250, at 230v a 11 amp motor would be 5Hp ish, would the disconnect need to handle the HP plus the heater..
in a google search at Home Depot disconnects. The 30 amp AC 240v disconnect (fused) is rated for 3hp...
http://www.homedepot.com/p/GE-30-Amp-120-240-Volt-240-Watt-Fused-AC-Disconnect-TF30RCP/100576894
With this disconnect, it says it's rated for 240 Watts ??? how can that be? is it only rated for 1 amp @ 3hp ???
This one is rated 7200watts but I see no Hp rating, assuming 3 HP ??
a 60 amp non fused disconnect
http://www.homedepot.com/p/Eaton-60-Amp-2-Pole-NEMA-3R-AC-Disconnect-AC222URNMP-A2/202106488
says 14400 watts but no mention of Hp, just AC.
this one is 60 amp non fused is rated 60 amps and for 240 watts ??? again? it's rated for 60 amps and 1 amp??
http://www.homedepot.com/p/GE-60-Am...C-_-NavPLPHorizontal1_rr-_-NA-_-100674085-_-N
What am I missing here?
Thank you
20 amp 120v. - with a switch on a wall for a timer. power>switch>tub
turns out the owner got a Kohler 240v unit with a heater
kohler underscore k1835h2
spec calls for hard wire 240v 20 amp... controls are in the unit.
(I may keep the switch location installed for future if someone rips out the kohler and sticks in a regular 120v unit, or rewire and just bring the feed to the tub area and install AC disconnect)
Evening thing is still open so it's not a problem to feed straight to tub and lose the wall switch.
The unit specs say the motor is 11 amps and the heater is 1500w..
I'm considering the ac "cheapo" water proof 30 amp pull out non fused disconnect. BUT ..
looking at 430.250, at 230v a 11 amp motor would be 5Hp ish, would the disconnect need to handle the HP plus the heater..
in a google search at Home Depot disconnects. The 30 amp AC 240v disconnect (fused) is rated for 3hp...
http://www.homedepot.com/p/GE-30-Amp-120-240-Volt-240-Watt-Fused-AC-Disconnect-TF30RCP/100576894
With this disconnect, it says it's rated for 240 Watts ??? how can that be? is it only rated for 1 amp @ 3hp ???
This one is rated 7200watts but I see no Hp rating, assuming 3 HP ??
a 60 amp non fused disconnect
http://www.homedepot.com/p/Eaton-60-Amp-2-Pole-NEMA-3R-AC-Disconnect-AC222URNMP-A2/202106488
says 14400 watts but no mention of Hp, just AC.
this one is 60 amp non fused is rated 60 amps and for 240 watts ??? again? it's rated for 60 amps and 1 amp??
http://www.homedepot.com/p/GE-60-Am...C-_-NavPLPHorizontal1_rr-_-NA-_-100674085-_-N
What am I missing here?