Mister.Soda
Member
- Location
- Boulder, CO
- Occupation
- Engineering Consultant
I have a client who is replacing a gas water heater in their utility room with a HPWH. The appliance branch circuit currently only feeds a washing machine that has a max power draw of ballpark 5A (slightly less). The branch circuit has a 20A breaker, is run on 12/2 wire, but interestingly, appears to only have 15A sockets.
Rheem makes two categories of 120v HPWH: one designed for shared 15A circuits (390 - 440W) and one designed for dedicated circuits (1100W). (Both mfr specs. I don't have access to the nameplates yet.)
The home outlets run at about 124V. In my mind, the 440W HPWH will draw about 3.7A (<4) and the 1100W ~9.2A (<10).
The 1100W version is preferable because of more than 2x faster recovery rates.
The 440W, <4A HPWH is a no-brainer, obviously fine. The question is, can the <10A HPWH be installed on this shared branch circuit?
NEC 422.13 indicates that a storage type water heater of 120 gallons or less shall be considered a continuous load, which requires a 125% continuous use factor for load calculations. And NEC 210.23(A)(2) says that on a multi-outlet branch circuit, the rating of cord-and-plug connected equipment fastened in place (like a water heater) shall not exceed 50% of the branch circuit rating, where lighting units or portable cord-and-plug connected equipment are also supplied from the branch circuit.
Without the 125% multiplier, the <10A HPWH should be fine on the circuit. When the HPWH and washer both run at full power, they're still drawing less than 15A.
However, my concern is that 125% multiplier. With the 125% multiplier, 9.2A becomes 11.5A, which exceeds the 50% limit of a multi-outlet branch circuit.
Client has a strong preference for the 1100W unit. I'm fine putting <15A of equipment on the 20A circuit, but am a bit shaky on whether this would pass code or not. Probably not? Interested in thoughts and feedback.
Cheers.
Rheem makes two categories of 120v HPWH: one designed for shared 15A circuits (390 - 440W) and one designed for dedicated circuits (1100W). (Both mfr specs. I don't have access to the nameplates yet.)
The home outlets run at about 124V. In my mind, the 440W HPWH will draw about 3.7A (<4) and the 1100W ~9.2A (<10).
The 1100W version is preferable because of more than 2x faster recovery rates.
The 440W, <4A HPWH is a no-brainer, obviously fine. The question is, can the <10A HPWH be installed on this shared branch circuit?
NEC 422.13 indicates that a storage type water heater of 120 gallons or less shall be considered a continuous load, which requires a 125% continuous use factor for load calculations. And NEC 210.23(A)(2) says that on a multi-outlet branch circuit, the rating of cord-and-plug connected equipment fastened in place (like a water heater) shall not exceed 50% of the branch circuit rating, where lighting units or portable cord-and-plug connected equipment are also supplied from the branch circuit.
Without the 125% multiplier, the <10A HPWH should be fine on the circuit. When the HPWH and washer both run at full power, they're still drawing less than 15A.
However, my concern is that 125% multiplier. With the 125% multiplier, 9.2A becomes 11.5A, which exceeds the 50% limit of a multi-outlet branch circuit.
Client has a strong preference for the 1100W unit. I'm fine putting <15A of equipment on the 20A circuit, but am a bit shaky on whether this would pass code or not. Probably not? Interested in thoughts and feedback.
Cheers.